After having a discussion with a colleague earlier today I was wondering what peoples preferred method is when testing prospective fault current on a three phase distribution board.

Do you:

A. Perform a 2 lead test between L1-E, L2-E, L3-E, L1-N, L2-N & L3-N then double the highest value.

Or

B. Perform a 2 lead test between L1-L2, L1-L3 & L2-L3 then record the highest value without the need to double?
 
I tend to do a line to neutral just to confirm the neutral is working. Then phase to phase to test between all three phases. Finally all phases to earth.
 
Just had a look through GN3 and apparently the most accurate way is to test between line - line and then divide the highest value by 0.87. I'm sure I wasn't told this on the 2391.

PicsArt_10-14-06.39.26.jpg
 

Reply to 3Phase PFC in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
653
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Regarding 3 phase IR tests for initial verification, I'm wondering how people actually do it efficiently. GN3 says to IR test between all phase...
Replies
4
Views
1K
Because none of us are beyond schoolboy errors.......... Doing some events kit testing over the weekend, some larger metal stand distro panels...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock