I admire you for tackling this. It is impossible for us to really comment on what you are up against, but from what you have described so far I think I would have offered 2 options regarding this setup.

1) New install to my design
2) Walk away.

Best of luck
 
One of the cables is a 2 core with a brass sheath used as a neutral.

Brass sheath?? Never seen or heard of such a cable system!!! Going purely on what you have written it sounds more like MICC, but illegally having the sheath used as the neutral conductor!! Almost like concentric wiring, but with a twist!! lol!! I would look into this cable configuration a lot deeper than you have, this sounds like a potential major cock-up waiting quietly to Bite!!!
 
Are these 25mm tails your describing coming into the house double insulated tails or are they an swa?
 
The tails (4 in total ) are in swa. This part look like it was done by the distributor but why they put the meters in an out house god only knows. Like I said it looks like it has been there at least 30-40 years.
It has to be the most bizare set up around.
 
The brass sheath you spoke about does sound like pyro (micc) which if it is an the sheath is used as a neutral then that is a problem which needs addressing. Can you post a picture up of this cable? I assume this then has a separate cpc wired with it? Good luck. Sounds as though you'll need it. Personally I'd have insisted a full EICR be carried out prior to any work and then quoted accordingly. As said in a previous post, certain items would need upgrading to my design or I'd also walk away.
 