Would you mind explaining what you need it for? ThanksI need a 40A single pole contactor. The main contacts to be normally closed in the distant passed I seem to remember you could get them.
Anyone know where to get them?
Thanks in advance
I have a client that wants to install 3 showers, the supply Is limited to 63Amp so I am looking into automating it so as only 1 shower can be used at a time. Current detection will be needed down stream hence the N/C line contacts.Would you mind explaining what you need it for? Thanks
Thanks DPG exactly what I am looking for ??Worth looking at a shower priority unit?