Discuss 4c10 micc feeding off peak and domestic DBs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all
Got 4c10mm micc supplies to off peak DB and domestic DB
Backed up by individual 80A Kmf s, what are your thoughts on two feeds in same micc.
Put appropriate warning labels on both ends
Down rated fuses to 63A
Multiple circuits in a single cable are completely compliant, no need for any special labelling.
80A down 10mm MICC doesn't sound like it's likely to be a problem. Although I note you say they are backed up by the 80A fuse, does this mean there is another fuse too?
As above does not require notices but 80A would be too high for the cable. Sheath is good for 10.0 bonding provided it is glanded off correctly.
Yes 100A met 16mm tails to meter then 16mm tails to 2 X 80A BS1361 swf Kmf. Put on report C3 tails need upgrading. Put on report 80A fuses need down grading for the the 4c10mm micc.cable properly terminated earth ring 10 mm earth bond both ends Sorry must remember to take pics. Thanks all
Reply to 4c10 micc feeding off peak and domestic DBs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Evening All Just want to check I've got his correct.... have a property with peak & off-peak DB. The tails from both DBs peak & off-peak go into...
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Is a board layed out like this correct for an eco 7 off peak supply and a peak supply? Two isolators that feed seperate rcds. They have a...
4K
I have a single 7kW EV charger that serves three holiday cottage. The supply to it is E7, with the night rate currently at exactly half the day...