just a quick one chaps, need to connect a 6kw domestic cooker, its wired in a 6mm radial on a 32a mcb. i have some 4mm heat resistant flex from work, is it ok to drop to the 4mm cable from the cooker outlet or do i need to stick with the 6mm csa. i work industrial/commercial so just after advice. thanks.
 
should be fine on 4mm HR. flex. don't forget diversity. doubt it will ever pull more than 20A.
 