A
and
Installers are here, they want to use 4mm for the 9m run of AC cable, I thought the general opinion was that 6mm was better, ie less of a power loss.
Quick reply needed!
Thanks!
From what I have read.... A 3kw system must have a minimum size of 4mm cable to a maximum length of 23m long, 6mm to 32 metres and after that 10mm.
"Refer to the 17th edition regs book, chapter 54 covers it.
To add a new circuit for PV requires Part p and full electrical certificate which includes uprating the earth . regulation 131.8 page 16 covers the issue."
As others have said, 4mm is fine. SB4000TL would have needed 6mm (although I doubt that it would make any difference anyway over that kind of length.
Well, the 4mm cable is in, I upgraded my gas/water mains earth to 10mm, the rails are on, panels going up tomorrow! ...
Don't quite understand why work out the volt drop on a 2.5mm cable? ... would like to understand ..
Not being an electrician I'm not really up on volt drop calcs ... but that was the essence of why I asked which is more suitable: 4mm or 6mm.
Power loss due to cable heating up, the hotter it gets the more reistance which makes it hotter, etc.
How much power loss will occur? Don't know!
I assume the 4mm cable coming off of the Power One 3600 putting out a max of 16A will get no hotter and offer no more resistance than a 6mm cable. A 2.5mm cable on the other hand, I assume, would indeed warm up ... ????
4mm or 6mm for 9m cable from inverter to CU
and,
and,