Discuss 50v on swa banjo ? TNC-S system new build in the UK Electrical Forum area at ElectriciansForums.net
I’ve had a weird one today. Banjo having 50v on it.
L - main earth = 230v
L - N = 230v
N - main earth = clear
I have 50v on the live - banjo & 24v on the Neutral - banjo.
Disconnected both sides of the armoured and done insulation resistance between all cables and all <999.
Have you done continuity tests on the SWA?
Where were your first and second test results carried out?
Surely the banjo is earthed if you are testing voltages to it, if you disconnected the earth to the banjo but the box or whatever its fitted to is screwed to a wall or something then you will still get some voltage between it and live.
L - N = 230v
What does clear mean? Is that 0V between them or no continuity between them?
Does the banjo have fly-leads fitted or is it one of the all-too-common wireless ones?
Did you test IR between the conductors and the armour?
Reply to 50v on swa banjo ? TNC-S system new build in the UK Electrical Forum area at ElectriciansForums.net
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...