Hi i see time and time again Electricians who connect either 6,10, or 16mm2 tails directly from the meter to feed a 1way unit for a shower or cooker etc, i never do it because i dont believe its the correct thing to do.

Obviously 6,10 or 16mm2 isnt rated at 100amps so if there is a fault on that piece of cable the fuse isnt going to blow the cable is goin to fail.

What are the regs on this?

Ive asked numerous people and noone can give me a straight answer, any ideas?

Cheers
 
I'm with you mark, i'll always use 25mm tails. I'm sure there was something at the front of the (old 16th) regs book or osg about it. Will see if i can find it again!!!
 
when i worked for the local electrity board this was completley acceptable,if you look at economy 7 time switches,only a 6mm tail would fit to trip the meter to "off peak" i think its covered in the supply regs,this is also the case where 16mm tails are protected by 100amp fuse as is common in south west,right or wrong is matter for debate.
 
May be common practice but - correct me if I'm wrong - isn't there somewhere in the Regs that says that the whole installation must be capable of being isolated from one switch - which in this instance would not be the case if you've got separate tails going straight from the meter to a 1 way unit and also to your main board.

As for size, I'm with slr - better to be safe than sorry. Interesting to read coomers inside knowledge tho'!
 
Hi i see time and time again Electricians who connect either 6,10, or 16mm2 tails directly from the meter to feed a 1way unit for a shower or cooker etc, i never do it because i dont believe its the correct thing to do.

Obviously 6,10 or 16mm2 isnt rated at 100amps so if there is a fault on that piece of cable the fuse isnt going to blow the cable is goin to fail.

What are the regs on this?

Ive asked numerous people and noone can give me a straight answer, any ideas?

Cheers


mark

you have to ask yourself what is protecting what

Lets say the tails are feeding a cooker circuit on a 32A type b 60898 MCB for example. The MCB is the overcurrent protective device for the circuit, so Ib In Iz complies

the 100A BS1361 fuse is the shortcircuit protection, and 6 mm tails WILL handle the fault current required to blow this
 

Reply to 6, 10 , 16mm2 tails from meter? in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock