juanpabs

Seen something today while performing a fire alarm test at a relatively sized office that struck me as strange. Thought there was no better place to query it than here. Like I said decent sized office, 3 phase tn-c-s supply can't really say too much more about the installation because this wasn't what I was there for, but i think I remember seeing 5 separate DBs on my way around so quite a large load yet only a 6mm earthing conductor! Now most commercial supply's I've seen have at least a 10mm earthing conductor, noticed the periodic warning which says it was done previously, less than 5 years ago! So I would presume that it all calculates correctly or this would have been sorted then?
 
A 6mm² earthing conductor would likely comply with the requirements for minimum csa as regards the fault current and was probably installed some time ago and has never been upgraded to meet the current requirements of minimum 10mm² for TNCS.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
6mm earthing conductor
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
2

Thread Tags

Advert

Thread statistics

Created
juanpabs,
Last reply from
Richard Burns,
Replies
2
Views
865

Advert

Back
Top