I'm looking at doing a CU change. Current main earthing and bonding conductors are both 6mm. Tails are 16mm on a 60/80 amp fuse (TNCS). ZE = 0.1 , 230v, single cable not bunched.

Looking at the regs (543.1.1) and applying the adiabatic equation (543.1.3), 6mm seems ok for main earthing conductor.

As for bonding, BPG1 states that 6mm will be ok if there is no sign of thermal damage.

It would be quite a job to replace so hoping not to.

Am I missing something glaringly obvious please? Thanks
 
Pre 16th Ed (15th Ed) the Regulations never quoted a minimum size for main protective bonding for TN-C-S supplies they suggested consulting the supply company, so with this in mind and assuming this is pre 16th Ed you will never know whether those conductors fulfilled the requirements of the time.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
6mm Main Earthing Conductor
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
deejay,
Last reply from
Lister1987,
Replies
3
Views
5,660

Advert

Back
Top