The spec is deta accessories.So true DW. First one I checked was Crabtree 50A and they won't accept bigger than 10mm2.
View attachment 37643
So I'll have a look , think they only go as far as a 45 amp DP switch.
Not sure on terminal size yet
The spec is deta accessories.So true DW. First one I checked was Crabtree 50A and they won't accept bigger than 10mm2.
View attachment 37643
Can only think running and terminating a 16mm2 T and E would be complete barsteward16mm for a bloody shower? bloody madness. these insulation freaks need to work round us and keep it away from cables. not vice versa.
May be a good idea to add to the 18th consultancy debate Tel, but never given that much thought to it, make you think though, good pointslightlyoff topic, but hre's something that has been bugging me for ages.
when applying the temp. factor ( 1.2 ) to your loop impedance as per osg., why apply it to the whole Zs value and not just to the R1+R2, when the supply cable from sub-station is never going to approach anything like 70 deg. ????
thoughts???
slightlyoff topic, but hre's something that has been bugging me for ages.
when applying the temp. factor ( 1.2 ) to your loop impedance as per osg., why apply it to the whole Zs value and not just to the R1+R2, when the supply cable from sub-station is never going to approach anything like 70 deg. ????
thoughts???
We do by doing the rule of thumb 80% values of those given in bs 7671.slightlyoff topic, but hre's something that has been bugging me for ages.
when applying the temp. factor ( 1.2 ) to your loop impedance as per osg., why apply it to the whole Zs value and not just to the R1+R2, when the supply cable from sub-station is never going to approach anything like 70 deg. ????
thoughts???
May be a good idea to add to the 18th consultancy debate Tel, but never given that much thought to it, make you think though, good pointslightlyoff topic, but hre's something that has been bugging me for ages.
when applying the temp. factor ( 1.2 ) to your loop impedance as per osg., why apply it to the whole Zs value and not just to the R1+R2, when the supply cable from sub-station is never going to approach anything like 70 deg. ????
thoughts???
slightlyoff topic, but hre's something that has been bugging me for ages.
when applying the temp. factor ( 1.2 ) to your loop impedance as per osg., why apply it to the whole Zs value and not just to the R1+R2, when the supply cable from sub-station is never going to approach anything like 70 deg. ????
thoughts???