The fact that only one wire was burnt suggests that the problem came from a loose/ faulty terminal or connection. Even thou the cable size is not adequate, it alone did not cause this, a bad connection caused this !
Discuss 8.5kw shower wires in 4mm, burnt terminals in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
slightlyoff topic, but hre's something that has been bugging me for ages.
when applying the temp. factor ( 1.2 ) to your loop impedance as per osg., why apply it to the whole Zs value and not just to the R1+R2, when the supply cable from sub-station is never going to approach anything like 70 deg. ????
thoughts???