For anyone bored by the constant myths and rumours regarding this subject, have a read of this guide from the IEE on supplies to detached outbuildings.
It was published in 2005 but the important bits remain unchanged and might be of some help!
Why not take the PME to the outbuilding/shed or whatever, and connect a rod to the EMT at the small CU?? You then have best of both worlds relatively speaking. Personally i wouldn't feel the need to rod, i'd be more than happy with the PME...
The way things are in modern times, is profits Rule!!! and it's how much that maintaining PME is going to eat into those profits that will decide. That and substantial fines and/or damages for Not maintaining their LV network earthing systems...
Well i think we are singing off the same hymn sheet, connecting an electrode system at the emt or met if at the correct Ra will maintain a safe touch voltage upon a broken pen, or do you mean take out the PME and the divorce the earth at entry?
Regards Chris
Regards Chris
Come on Chris, why would i want to ditch a superior earth and replace it with a TT system!! ...lol!!!
As i said in my post above i wouldn't feel the need to add an earth electrode to the EMT of an outbuilding. But if there was an existing rod in place, near to the outbuilding, of course i'd certainly make use of it!!
Lol, when i was replying i thought as much, just testing :).
Regards Chris
one thing this whole topic has made me think about is that when I happen to be taking a 10mm sub main or bigger to an out building I automatically have an earth wire large enough to cope with bonding, so or though I would normally make this area TT I could legitimately connect it to the PME incomer.
Yes if the CPC of the sub main is 10mm² copper, then it could be used as a bonding conductor.
The problem being that the armour of 10mm² SWA being steel, does not have an equivelant conductance to 10mm² copper.
Thsi leaves you with the choices of 2 core SWA and a rod, 2 core SWA and a separate bonding conductor or 3 core SWA.
Thanks for this, very useful and I understand what has been explained about the myths of exporting PME.
I am connecting a garage 45m to the CU in the house on a TNC S and have decided to connect by means of 2 core armoured cable. I shall be adopting a TT system in the garage with an earth rod. The armour will of course only be connected at the house CU.
My question is about discrimination of the RCD's. The MCB for the garage, in the house is protected by a 30mA RCD and the socket circuit in the garage requires a 30mA RCD. What is the best way to achieve discrimination of the RCD's? If I replace the house RCD with a slow 30mA would this contravene the regs on the other circuits protected by it. thanks
What do you mean by ''Slow 30mA'', do you mean an S type RCD?? How are you going to do that then?? Any other circuits on that S type RCD will not meet BS 7671 requirements!!
Either a non protected MCB in the CU, or Henley Blocked tails with a 100mA S type RCD.
And if there isn't any extraneous services at this garage, then you would be much better off, taking the PME earthing with you from the house!!
Can someone please fill in the blanks for me as I'm really interested in this topic but strugling with a few bits.
If you have an outbuilding which you install Db2 with say lighting and power radial circuits as part of a PME system then any copper water bond would have to be connected in 10mm to the DB1 MET.
Now as you have sized your submain to DB2 as 4mm, rather than running a 10mm back to the supply origin you elect to make the out building a TT system. You connect your spike with 6mm and connect to DB2 (all going well) but then there is the copper water pipe. Minimum bonding conductor is 6mm (pretty sure half of line or neutral conductor or 6mm minimum for non PME) but does it matter that this is larger than our line and neutral conductor?
It just seems a bit odd with a 6mm earth and a smaller line and Neutral. If ive got this way wrong please dont bite my head off.
If you don't understand something, just ask, don't bother with the abusive comments.
A good guide, am pricing to install heat light and power to out building 35 m from main board. Installing new circuit on none rcd side of split board to 32amp mcb in 4mm armoured clipped and buried to 2nd rcd db in shed with 4 ways, 1 for heater, 1 for sockets, 1 for light and a spare for garden lights heat and power on 20a each and lights on 6a.
Luckily no metal work to bond to complicate matters!
actually I do,but it seems a lot of people do not understand the differences between TNCS and PME.
they would much rather give out what may well be potentially lethal advice!
it appears more and more frequently that earthing systems seem to be very much misunderstood by far too many people that claim to be competent electricians.
Perhaps you could explain it to us then??
a really easy point to make would be that PME and TNCS are NOT the same thing,
far too many so called 'competent' 'electricians' seem to think they are,
there is a world apart from the 2 systems described by TNCS and PME,
if you actually know what the letters stand for then you should also know what the differences are.
and its not always a good thing to believe what the DNO may tell you or label your cut-out up as,
I know we are supposed to take that as being correct, but I for one am not willing to put someones life at risk for the sake of a sticker on the incoming fuse.
PME- protective multiple earthing, which means that the PEN conductor is grounded at many points along its path.
TNC-S, the PEN conductor is split at the service head, to from as neutral and an earth conductor. There is nothing to say that the PEN conductor is earthed on its way from the tranny.
Its good practice to install your own rod, to help stop diverted neutral currents appearing on your installation.
it is, but without a proper knowledge of the systems involved and adequate labelling, it unfortunately very seldom happens,
and that is where a very inherent danger occurs from a very substantial number of sparks.
A good guide For 'exported PME' and outbuildings!
Australia
IQ Electrical,
Dan,