Twin and earth is not suitable for "flexible" applications such as this.

For most extension leads the choice would normally be 1.5mm 3-core so it is rated at the full 13A. If indoors then you can choose whatever type/colour you like (but for outdoors use something like H07RN-F rubber cable as it is tough and UV-resistant).
 
Example of the rubber flex (sold by the metre):
 
Typically PVC wire is sold in reels or significant sections, this might do as a cheap-ish option:
https://www.NoLinkingToThis/p/time-3183y-white-3-core-1-5mm-flexible-cable-10m-coil/342jy

But you might find it as cheap to simply buy a made-up lead in the first place!
 
Hell folks,

I need to make up a 4 metre extension lead to take a TV and a DVD player. Can someone please advise as to what size twin and earth cable will be suitable for this.

Many thanks.
.Just go to your local DIY or electrical outlet and purchase a propriety extension lea, B&Q sell them as do Homebase. wast of time and money making your own, in my opinion.
 
As above, do not use 6242Y or similar solid conductor 'twin and earth' cable; it is only suitable for permanently installed, immovable wiring. Ordinary 3183Y PVC circular flex is the usual choice for indoor domestic purposes.

Commercial 13A-rated extensions and appliances are normally fitted with 1.25mm² cable, which has a rating of 13A in free air. However, 1.25mm² flex is not widely available in shops. 1.5mm² is common, rated at 15A and is the largest cable that 13A plugs and trailing sockets are designed to accept. Extensions made with either of these two sizes of cable may be used for any purpose since the cable is of equal or higher rating than the plug.

The combined load of the TV and DVD player will not be more than a couple of amps, so in theory a smaller cable could be used. However, it would be reliant on the correct plug fuse being fitted for protection and could not be pressed into service for a higher load application, or might overheat if this was not observed. Personally, I detest under-rated extensions; life is too short to faff around with one cable rated at 10A vs. another rated at 13A. Any lead I make for any purpose is fully rated to 13A and I need not think about it any further. I recommend the same here.

TL, DR; 1.5mm² 3183Y circular PVC flex.
 
As above, do not use 6242Y or similar solid conductor 'twin and earth' cable; it is only suitable for permanently installed, immovable wiring. Ordinary 3183Y PVC circular flex is the usual choice for indoor domestic purposes.

Commercial 13A-rated extensions and appliances are normally fitted with 1.25mm² cable, which has a rating of 13A in free air. However, 1.25mm² flex is not widely available in shops. 1.5mm² is common, rated at 15A and is the largest cable that 13A plugs and trailing sockets are designed to accept. Extensions made with either of these two sizes of cable may be used for any purpose since the cable is of equal or higher rating than the plug.

The combined load of the TV and DVD player will not be more than a couple of amps, so in theory a smaller cable could be used. However, it would be reliant on the correct plug fuse being fitted for protection and could not be pressed into service for a higher load application, or might overheat if this was not observed. Personally, I detest under-rated extensions; life is too short to faff around with one cable rated at 10A vs. another rated at 13A. Any lead I make for any purpose is fully rated to 13A and I need not think about it any further. I recommend the same here.

TL, DR; 1.5mm² 3183Y circular PVC flex.
Thank you for this comprehensive response Lucien, much appreciated. The identification number of the cable is most helpful. I'll get on with the job now. Thanks again.
 

Reply to A little wiring help please. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
837
Help please! Got this to use as a doorbell but unsure of specifics and wiring. If someone could maybe help with a diagram/specific parts or even...
Replies
11
Views
552
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
289
Hi Folks, I wonder if someone would be good enough to help, please. I have a new light fitting that has 2 slots, one for live and one for...
Replies
10
Views
1K
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock