To answer your question, yes you can add RCD protection to just the ring circuit as you described.
Excuse the possible numpty question but if you've got a ring final circuit, how do you add external RCD protection to it? Radial yes, obvious, but ring? (I can think of possible ways but I'd rather hear your answers.)
From CU to external RCD, then connect ring feed/return to that. Daz
So just suitably sized single cable CU to RCD, say 6mm (depending on OCPD at CU, reference method, etc.)? And in effect call that a distribution circuit and then the RCD a new DB? (Just thinking about how you'd test and document it on the sheets, cos obviously the usual ring tests wouldn't work if carried out at the original CU cos then you're testing a ring fed from a radial, which is what, a lollipop?)
So your sister is spending £1000's on a new kitchen, and then skimps by poncing around with a separate external RCD box just for the kitchen sockets, ... in god's name WHY??
How much more will it cost to replace the existing 3036 CU for a 17th ed CU that will give additional protection to the whole house?? This situation never ceases to amaze me, and as an electrician, why you would even contemplate doing it, especially as you are talking about your sister families house...