it's not a spur off a spur. it's multiple sockets on a spur.
Apologies for my lax terminology. But you get my point eh Tel.
it's not a spur off a spur. it's multiple sockets on a spur.
And does not contravene the regs.
yes it does, as you have a single 2.5mm T/E cable protected by a 32A MCB. so In> Iz.And does not contravene the regs.
Possibly.So a question - would you be happy to have 5 double sockets connected as a spur from a socket on an RFC?
Possibly.
They help the OP, by helping him, and everybody else, to actually THINK.
Think about how circuits work.
Think about what cable(s) you need for given loads.
Think about what you'd have to do to put 2 sockets on a radial cable.
THINK.
It is a valid design, which also meets the desirable requirement for DP isolation.And a suggestion was made to use an FCU to feed the OPs extra sockets. I think this is a fair idea. Don't you?