I would suggest that if you do the inspection and testing and find that the circuit is non complaint that you then do not issue a MEIWC, but instead provide written advice to the customer of the problem with the circuit and the level of urgency with which it should be addressed.
I changed some light fittings on a TT installation and then checked the circuit and found no RCD protection on the circuit as it had been removed by a previous "electrician" to "resolve" the tripping problem.
I advised the customer in detail of the dangers involved especially considering most of their lights were class I (but not mine) and provided the option of an RCBO solution but they decided to leave it as it was!
OK customer informed, job complete, move on.
Just covering your behind basically, whilst at the same time making the customer aware of the potential dangers.
In that case i would suggest just issuing the client some written proof that you have acknowledged the installation is not up to standard and get them to sign something to cover yourself.
I expect one of the more seasoned members will be able to give a more definite answer though mate. :)
Issue the MNWC and note any problems you ind in the comments section, quite simple really.
It will always be mixed opinions depending on the electrician i suppose. As long as its all above board and communicated effectively then i see no issue either way. :)
hightower,
Simonslimline,