Hi guys,

I had a brain fog on the adiabatic.
Trying to ascertain suitability of a 6mm bonding conductor in a domestic installation. Doesn't help that I forgot my regs book too!

I have a pefc of 1.17KA. Can anyone help please?

Thanks.
 
Quiet this morning!
My thoughts were that if I could prove minimum size of the main installation earthing conductor and then use the 50% rule for the main bonding conductor it might come out at <6mm. Although I have just noticed that the installation has TNCS earthing! Does this mean I can't calculate and have to select from table??

Any help please?
 
Thanks Ian. Yes I know that's why that's why I was using the equation to size the installation earthing conductor and using the 50% rule to then size my bonding conductor. But in the absence of any books I couldn't remember whether I could that for a tncs installation?
 
Thanks Ian. Yes I know that's why that's why I was using the equation to size the installation earthing conductor and using the 50% rule to then size my bonding conductor. But in the absence of any books I couldn't remember whether I could that for a tncs installation?
on a TNC-S installation min. size for bonding conductors is 10mm.
 
As said, 10mm is the minimum bonding conductor size, an existing 6mm tho doesn’t necessarily make an installation unsatisfactory.
Your earthing conductor would also need to be 10mm minimum if it’s a combination of protective bonding conductor and main earthing conductor.
 
As said, 10mm is the minimum bonding conductor size, an existing 6mm tho doesn’t necessarily make an installation unsatisfactory.
Your earthing conductor would also need to be 10mm minimum if it’s a combination of protective bonding conductor and main earthing conductor.
We're doing remedials at this installation, including a consumer unit upgrade. The route for rewiring the bonding conductor is unbelievably difficult! Is there any way I can risk assess to get around rewiring this 6mm bonding conductor? ?
 
Off on a bit of a tangent, but an niceic tech rep told me once on the phone about a calc that is in either the iet design guide or e&b guidance note (can't remember which) that can be done using either R2 or IR reading between a service pipe and the MET to prove whether is a genuine extrenuous conductive part which needs bonding.

Dont suppose anyone knows what I'm talking about do they?...
 
Off on a bit of a tangent, but an niceic tech rep told me once on the phone about a calc that is in either the iet design guide or e&b guidance note (can't remember which) that can be done using either R2 or IR reading between a service pipe and the MET to prove whether is a genuine extrenuous conductive part which needs bonding.

Dont suppose anyone knows what I'm talking about do they?...

I think you are talking about the test to prove whether an item is an extraneous part or not.
 
main bonding protective conductors are sized by the Relevant table in the IEE REGS, not by adiabactic equation.
i just use whatever i find first on the van. still got a roll of plain green. (imperial). think it still has the price on the 100 yard drum.... £1.10.,6d.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

spud1

Arms
-
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Adiabatic equation help
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
spud1,
Last reply from
spud1,
Replies
15
Views
3,020

Advert

Back
Top