Well the 5 lights work fine on either a 10A Type B or a 6A Type C, so I should be ok with all 10 on a 20A Type B or possible a 10A Type C. Also the next 5 will be switched separately so that will avoid the inrush current of all 10 at the same time. Happy :)
Until some body switches, all of the lights on at once, you just know it's going to happen Murphy's Law dictates this.
 
You can find the time Vs current curves for type b,c,d MCB in the installation and test regulations.
Type B instantaneous trip is 3-5 times rating
Type C instantaneous trip is 5-10 times rating
Type D instantaneous trip is 10-20 times rating

This is the magnetic trip and applies to inrush current.

I should add that the current is RMS current, so averaged over 1 half cycle. So very high inrush currents lasting less than half a cycle might not trip the MCB if the average over that cycle is lower than the trip characteristics.
 