The cable MUST be selected according to the rating of the protective device, In - not the anticipated load.
Why? Under fault conditions current up to the rated current of the protective device MAY be drawn through that cable. An extreme fault condition is a nail through the cable, but a shorted turn on a heating element is a more subtle yet possible fault which would result in higher current than when operating normally.
Therfore, to re-iterate .... Select the cable in accordance with the protective device and any rating factors which result for the planned installation method. 40A MCB and 4mm T&E .... not a winning combination!
fault current may be well in excess of the rated current . even a 150% of the rating will not cause the device to operate for quite a while. it.s the duration of the fault current as well as the magnitude that matters. a 6mm cable may withstand a fault current of 400A without damage as long as the duration is limited by the speed at which the fuse/MCB trips.