Earth Rods are being hit in to their entire length, approx 1m deep, cannot get much deeper as we are hitting bedrook, have tested using |KEW-5105A and then tried removing the earth rood and testing again 1 meter further away from the property and so on, but cannot get the reading to get any lower. The soil is not the best, looks as though its had about 100 years of tiles, bricks and plaster pored into it.
1m is not deep enough to get an Ra which is stable long-term.
And using just one rod is not a very good plan either.
You need to go deeper or else find another method of installing an earth electrode