Hi Guys
Been reading this thread with interest, something worries me, I was always under the impression (my BS7671 is in my desk at work so I can't check) that you shouldn't use Flex to hard wire anything, and it shouldn't be used as part of the fixed installation apart from short lengths connecting power consuming apparatus to the fixed installation, I'll check on Wednesday when I'm back at work if only to ease my troubled mind.
 
OK chaps.

Here it is. BS 7671:2008 Amdt. 1, Section 521.9.1:

"A flexible cable shall be used for fixed wiring only where the relevant provisions of the Regulations are met. Flexible cables used for fixed wiring shall be of the heavy duty type unless the risk of damage during installation and service, due to impact or other mechanical stresses, is low or has been minimized or protection against mechanical damage is provided.

NOTE: Descriptions of light, normal and heavy duty types are given in BS 7540."


So there you have it. Acceptable, but with conditions.
 
There's the rub the O/P stated FLEX as opposed to flexible cable, there is a difference, perhaps I'm being picky. you are all bound to let me know.
 
There's the rub the O/P stated FLEX as opposed to flexible cable, there is a difference, perhaps I'm being picky. you are all bound to let me know.
All the same now, flexible cord was deleted in the last amendment, now says see flexible cable
 
OKY DOKY Cheers, not doubting what you are saying in any way, so we can, in theory use Flexible cable for anything we like then? a retrograde step if ever I heard one
 
You do need to adjust the current carrying capacity and volt drops as per Appendix 4, section 2.4. Other than that, how is it any different?
 
OKY DOKY Cheers, not doubting what you are saying in any way, so we can, in theory use Flexible cable for anything we like then? a retrograde step if ever I heard one

Provided it is suitable for the purpose and environment, and of suitable construction/protection if there is deemed to be a risk of damage.

Nobody uses flex for fixed wiring, like you say it doesn't make any sense to. But the original question was if it was against regs.
 
Sorry AndyL I'm Old School and it doesn't seem right, not saying you are wrong just don't like it
 
No probs Pete, I agree I wouldn't run it that way, but its already in and not against any regs
 
It is not against regs, that said it is a Crap Job. As for the certificate, anyone installing a new circuit should issue the customer with a certificate, even if it is just a results sheet to prove the installation had been tested and was left safe and sound.
 
I'm sure I read somewhere in the BGB that the length of flex is limited to 3 meters. IE from spur to appliance only. I may be wrong
 
Hi Camerabloke long time no see, seems that it cant be called flexible cord according to the regs it's flexible cable, cant say I like it though
 
I'm sure I read somewhere in the BGB that the length of flex is limited to 3 meters. IE from spur to appliance only. I may be wrong


Better let all the wholesalers, DIY sheds and other electrical outlets that they can no longer sell extension leads or drums of flex anymore then.
 