T
Toneyz
Sorry I don't know how to post up a youtube link but have a look at the John Ward one part 2 on AFDD's worth a watch.
I know, I have access to the standard.Just to put it into context, if it was a 32A AFDD then it would be about 5A![]()
You are correct, in that RCD's do not protect against series faults, such as broken conductors, we have MCB's to protect against L-N faults.J.W. has just posted the third video with an electric heater and it still did not trip. RCD's are ok for faults to earth not sure regarding L-N and broken conductors. Look forward to the replies.
A 300mA RCD is not going to trip in the event of a fire, until the cables have melted enough, to allow earth leakage to occur.Don't forget, I mentioned nothing about additional protection by RCD, i.e. a 30mA device, I was referring to 0.3A devices, 300mA, for prevention of fire, as per BS7671 clause 422.3.9.
Confirmation bias they call it.It's easy to make people believe rubbish, when they don't like thinks in the first place. It falls into their beliefs.
I can't take the credit for this @essex as it was a mate at work that pointed it out to me. I was initially a sheep, like most, who believed that the AFDD's should be detecting most arks.
As @netblindpaul has pointed out "If, the maximum fault energy to cause a fire is required to be limited by an RCD to 0.3^2 x t, then why is it allowed to be 2.5^2 x t for an AFDD?"
I presume it's down to cost. When you look at how the AFDD's detect arks then if they were to detect 30mA then there is going to be lots of nuisance tripping, unless the detection device is more fine tuned. This will increase the cost of these even more.