EXCEPT PME supplies
quote me the reg. for that.
EXCEPT PME supplies
only thing you got wrong there is the value of t. if it's a 100A BS88-3, t would be 0.2. an 80A fuse would be 0.1 ( fig. 3A1, BGB), so trhat would give you an even smaller csa for the MEC.
542.3.1 which in turn points to 544.1.1
Now although 5441.1.1 refers to bonding conductors, 542.3.1 also says where PME is concerned the earthing conductor shall also meet csa of MPB in 544.1.1
unless I am misinterpreting that reg
So, by that argument, there was a 16mm neutral, so 10mm main earth is the minimum (which in this case, it was)