J

Josh Tinto

So im currently doing my AM2 and doing the testing, I understand that this is simple, but when writing down the R1+R2 on the certificate, do I need to put the highest reading down? Theres a ring circuit eith 4 sockets on it l, however one of the sockets is a spur - which obviously has the higher R1+R2 reading, the readings I got were 0.04, 0.05, 0.06 and I got 0.12 for the socket spur, does that mean I have to put the reading I got for the spur in my certificate or do I take the highest reading from one of the sockets in the ring?
 
Highest reading for your R1+R2, same applies for your end to end readings but remember your line and neutral measurement should be the same with your CPC being higher.
 

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Thread statistics

Created
Josh Tinto,
Last reply from
Andy5678,
Replies
2
Views
2,762
Back