Josh Tinto

So im currently doing my AM2 and doing the testing, I understand that this is simple, but when writing down the R1+R2 on the certificate, do I need to put the highest reading down? Theres a ring circuit eith 4 sockets on it l, however one of the sockets is a spur - which obviously has the higher R1+R2 reading, the readings I got were 0.04, 0.05, 0.06 and I got 0.12 for the socket spur, does that mean I have to put the reading I got for the spur in my certificate or do I take the highest reading from one of the sockets in the ring?
 
Highest reading for your R1+R2, same applies for your end to end readings but remember your line and neutral measurement should be the same with your CPC being higher.
 