I think it was mentioned somewhere on another thread that Aico alarms have surge protection built in.
All competent mains powered electronics has some degree of surge protection simply to meet the minimum EMC regulations for immunity. However, it is usually only for small surges (typically 1.5kV is specified) and from not-very-low impedance sources (ie. the CAT-III sort of location at end of final circuit).

Having a SPD at the DB should keep any surges down-stream to under that sort of value, and so they can then deal with the short over-voltage OK.

As for the "10m distance" aspect it is more complicated. If you are trying to coordinate SPD (say Type 1 at input, Type 2 and DB further away) then you want the first SPD (high power, higher flash-over voltage) to conduct first, and only what gets past is then clamped by the second lower-power / lower-voltage SPD. To achieve that selectivity you need some impedance, and for that read inductance, so usually a minimum of 10m of cable, or a dedicated air-cored coil (rare). Inductors often have ferrite or iron cores to increase inductance for a given size, but under big surge conditions those cores saturate and the inductance plunges to the air-cored equivalent, so you might as well go for air-cored to begin with!

It is also highly dependent on what you are trying to protect, and where the lighting might hit. In most cases it is a far away strike coming in via power cables and the first SPD it finds does the job. If very near than all sorts of cables within the installation and/or to extraneous parts can pick up the induced current and cause grief. Usually I would only see the point in a SPD at a sub-board if very far away or other reasons to expect high local current (LPS present, big motors likely to dump switch off spikes, etc, etc).
 
Last edited:
Just to say I have used the Kingsmill stuff and they are good, if not cheap. But you also have to balance the realistic needs for protection in a given type of installation against what they are trying to sell!
 

Reply to Amd2 SPD on smoke alarms in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
353
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
544
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
946
Need advice please, I've been reading alot on spds and came across this, please read the picture I have posted, I am querying "equipment" if the...
Replies
1
Views
1K
Hi all! This weekend we have an offer on 8 of our most popular Smoke, Heat & CO alarms from trusted brands! Don't wait too long as these offers...
Replies
0
Views
386

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock