1pm, quite happy doing my planned job. Builder then asks if I could go out to another job where the top lights have all tripped out.
I like peace and quiet when fault finding, plus I like to plan it in advance and always first thing in the morning as you know it can get pretty complicated and I like to have a clear head, so I'm already off to a bad start. Plus, it turns out to be a noisy and busy work site.
6A MCB is tripping (not the RCD). IR test at 500V shows 0.01Mohms L-E. I then decide to use a smaller easier to use continuity tester (my big error) and get 80ohms between L-E, so basically I've got a short. Easy track down I think.
Narrow it down (using continuity tester) to a single piece of cable. The faulty cable has a joint in it (wago's). I disconnect the wago's to test either side in order to see which side of the cable has the fault.... and the fault has disappeared. I assume it was something to do with the wago's or the cable going into the wago's. I strip back, use new wago's, connect up, fault reappears. Disconnect, fault has gone from both sides of cable! I then connect up again and the fault has gone. It seems to come and go. It's 5pm. I leave the customer with all top lights working bar bathroom (I have disconnected the cable that sometimes tests faulty).
Go back today with a clear head. Continuity test again, all clear. Within a few seconds I am thinking why am I not IR testing? I'm just sticking to an easy continuity test as I got a few hits from that to begin with. IR test at 500V is a bit odd, changing from 5 or 6 Mohms to 0.3Mohms during testing. Still nowhere near a short circuit.
I test at 1000V (which isn't really on my radar) as i'm thinking burnt out section and it ranges from 5 Mohms to zero Mohms.
I pull out the faulty piece of cable from inside the wall (drawing new cable in). It looks absolutely fine. No visible damage at all and I have run my hand along every single inch of it, slowly and carefully.
I then cut in half etc etc and keep testing as i'm intrigued. I eventually find an incredibly thin stanley knife slice in it. I strip back the outer sheathing (which looks fine) and find this...

The line is almost completely severed.
I realise you guys may have come across this lots, so I'm a little embarrassed at being so excited about it (even more embarrassed at not testing correctly to begin with), but I'm still feeling chuffed at finding it
I like peace and quiet when fault finding, plus I like to plan it in advance and always first thing in the morning as you know it can get pretty complicated and I like to have a clear head, so I'm already off to a bad start. Plus, it turns out to be a noisy and busy work site.
6A MCB is tripping (not the RCD). IR test at 500V shows 0.01Mohms L-E. I then decide to use a smaller easier to use continuity tester (my big error) and get 80ohms between L-E, so basically I've got a short. Easy track down I think.
Narrow it down (using continuity tester) to a single piece of cable. The faulty cable has a joint in it (wago's). I disconnect the wago's to test either side in order to see which side of the cable has the fault.... and the fault has disappeared. I assume it was something to do with the wago's or the cable going into the wago's. I strip back, use new wago's, connect up, fault reappears. Disconnect, fault has gone from both sides of cable! I then connect up again and the fault has gone. It seems to come and go. It's 5pm. I leave the customer with all top lights working bar bathroom (I have disconnected the cable that sometimes tests faulty).
Go back today with a clear head. Continuity test again, all clear. Within a few seconds I am thinking why am I not IR testing? I'm just sticking to an easy continuity test as I got a few hits from that to begin with. IR test at 500V is a bit odd, changing from 5 or 6 Mohms to 0.3Mohms during testing. Still nowhere near a short circuit.
I test at 1000V (which isn't really on my radar) as i'm thinking burnt out section and it ranges from 5 Mohms to zero Mohms.
I pull out the faulty piece of cable from inside the wall (drawing new cable in). It looks absolutely fine. No visible damage at all and I have run my hand along every single inch of it, slowly and carefully.
I then cut in half etc etc and keep testing as i'm intrigued. I eventually find an incredibly thin stanley knife slice in it. I strip back the outer sheathing (which looks fine) and find this...

The line is almost completely severed.
I realise you guys may have come across this lots, so I'm a little embarrassed at being so excited about it (even more embarrassed at not testing correctly to begin with), but I'm still feeling chuffed at finding it