Discuss Another ceiling light question. in the Canada area at ElectriciansForums.net

U

Unclebill

We are refurbishing a room and on trying to replace old ceiling light I found that there are only two wires sticking out of a metal tube conduit both of which are red. The new fitting has a transformer so I'm assuming that it should be wired as the instructions suggest, live to live, neutral to neutral and earth to earth.
Only problem is there is no earth and, as stated before, both cables are red.
How do I find out which of the two wires go where and how do I fit an earth?
All suggestions gratefully received!!!
 
I could be wrong but if theres no earth, aren't you meant to fit class 2 fittings? and with the 2 red cables, I'm not too sure, maybe one of them is neutrel and hasnt been flagged up? they could ran out of cable and only had red/red twin?? I'll let the experts comment on this!! hang on tight!!

regards luke (please correct me if i am wrong)
 
Uncle Bill

it is likely that the metal conduit is being used as the earth, this is standard practice with metal conduit or trunking

Assuming you have a test meter, and assuming that one of the reds is an unsleeved neutral, then measring between both reds will show 230V, measuring between one of the reds and the conduit will show 230V, this is your phase conductor (and also proves the conduit is earth), then measure the other conductor to conduit should show 0V, this is your neutral and should be sleeved black.

Obviously working safely, etc etc

regards

Tony
 
Thank you Tony.
One point, should these measurements be made with the light switch on or off (probably a very stupid question!!)
Also, what can one do when there is no measurement equipment available??
Yours
Bill
 
Unclebill

The light switch would need to be on to power up the circuit. i would suggest terminating the cables in chockblock so they dont touch

Not much can be done without a meter. For a simple voltage test like this, one of the 10 quid argos digital multimeters would be sufficient.

You could also use a test lamp, but this would not give an accurate result of whether or not the steel conduit was properly earthed

regards

Tony
 
Multimeter worked a treat and the conduit pipe is the earth. Used an Ezybond earth clamp and the new fitting is up and running. Thanks to everyone who helped.
Bill
 

Reply to Another ceiling light question. in the Canada area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
369
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
633
Hi, I need some advice on the wiring for a new ceiling light. I have taken down the original light, and I'm left with the wiring in the image...
Replies
6
Views
1K
Hello everyone, hope all are well. I'm changing a ceiling rose and have lost the diagram showing where everything was connected (to the old light)...
Replies
8
Views
868
Just replacing a ceiling light and could do with some guidance on sorting out all the wiring. This is how it was: And the light is expecting...
Replies
1
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock