R
Redvanman
So here's the scene
All bonding, impedance values, RCD protection in place.
1) Inside the bathroom outside of the zones a underfloor controller has been installed with no local isolation (wired straight from the board)
I am thinking that its not a code, maybe a note as the only reg i can think of is 701.512.2 but that is only inside a zone but the controller is not suitable for the environment IMO ?
2)Cooker switch behind a built in double oven plus the cable is not long enough to place oven on the floor.
Now I am thinking a C3 because of reg 132.12 as the cable is to short but the switch behind the oven puzzles me because the MCB could be deemed as a isolator but there is another in the circuit that is not easily accessible.
3) Single socket behind a built in fridge/freezer.
Again I'm thinking C3 because of the above reg and 132.15.1.
I read these as being accessible for testing (no its behind a built in unit) and ability to isolate the appliance effectively (again no because its behind a built in unit)
So there's my questions and thoughts what do you guys think.
So here's the scene
(1) is there a fuse in the controller protecting the underfloor heating?
(2) can you clarify, sorry mate a little confused with 2
(3) is the single socket switched from a spur which is accessable?
Sorry a bit more info
No fuse but rated at 16 amps protected straight from a 16A MCB
The cooker switch is behind the built in oven and the only way to get to the switch is by taking the oven out and the cable from the switch to the oven isn't long enough to sit the oven on the floor when you've taken it out
No there,s no spur just the single socket
Code 3 for the heating as there's no local isolation and an MCB is not classed as an isolator.
Cooker switch also code 3 as it is inaccessible and besides which should be away from the cooker due to thermal issues. Cable too short would only really be a comment. I use the code "info" quite often in eicrs. At least that way you have made the client aware that there may be an issue there.
Fridge socket is just a comment at best. To be honest if any repairs were required to the fridge it would need to be moved anyway.
for me 1. is not complying with manuf instructions, the other two dont sound like much of a problem. Cable too short is a pain and worth a comment.
An MCB not a isolator? really?
Some UFH controllers have their own integral on/off switch.
'MCB is not classed as an isolator' see Table 53.4
Which reg says there has to be local isolation?