Evening all..
The customer has a cooker supply from CU - cooker outlet plate all in 6mm.
The new oven is 7.9kW and will be on a 32A MCB.
The new oven is encapsulated in the shed at the moment so I cannot get to the maufacturers instructions.
With diversity applied the load will be 17.31A (no socket on the cooker switch).
I would normally use 6mm twin and earth for this but I have had 50m of 4mm H07 rubber flex for a couple of years now, bought specifically for ovens/hobs (as one set of manufacturers instructions stated this so I went and bought 50m!!) but I never use it as it just feels wrong for a 7.9kW load!!
We would happily use 4mm for a radial on a 32A MCB.
Would you guys be happy to use 4mm from outlet plate to cooker (assuming manufacturers instructions do not stipulate anything)?
Cheers..