Evening all..

The customer has a cooker supply from CU - cooker outlet plate all in 6mm.

The new oven is 7.9kW and will be on a 32A MCB.

The new oven is encapsulated in the shed at the moment so I cannot get to the maufacturers instructions.

With diversity applied the load will be 17.31A (no socket on the cooker switch).

I would normally use 6mm twin and earth for this but I have had 50m of 4mm H07 rubber flex for a couple of years now, bought specifically for ovens/hobs (as one set of manufacturers instructions stated this so I went and bought 50m!!) but I never use it as it just feels wrong for a 7.9kW load!!

We would happily use 4mm for a radial on a 32A MCB.

Would you guys be happy to use 4mm from outlet plate to cooker (assuming manufacturers instructions do not stipulate anything)?

Cheers..
 
Get the 4mm in HHD. It would need some serious derating to be no good. I always use H07 for ovens - even if integrated.

Then Dave throws that in. ^^^^^^^^

Google the model for MI's mate.
 
I can't see why you would go to the expense of H07 for a cooker connection when T&E is perfectly adequate?

Personal preference, although I find H07 type cable is often stipulated. There is something about T&E left hanging down I just don't like.
 
I looked at an oven yesterday funnily enough, there was no outlet plate and just a load of twin and Earth hanging out the wall, they are buying a new one so will fit a proper outlet and put flex on instead.

I i prefere flex as when you push the oven in, it tends to sit better and move out the way without kinking or damaging it.
 

Reply to Another cooker thread and which cable I'm afraid? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
593
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
754
Hi all, I'm getting a 32a induction hob and a 13a oven installed as part of a kitchen refurb. The existing cooker circuit is 6mm protected by a...
Replies
7
Views
2K
I'd appreciate a quick sanity check, thanks in advance: New circuit for a 3 phase cooker, in a community centre (run by a charity). Total load...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock