Hope everyone else is having a better day than I had. Doing remedials for a landlord via a builder wasn't the best start.

The EICR looked semi decent on paper initially in that some of the tests appeared genuine, but turned out to be false hope. - Perhaps they thought the box marked Unsatisfactory on the front was meant to apply to the report, not the installation?

I found 10 errors (not matters of interpretation, but actual errors), in the first five minutes.

If I get bored enough, I might post a full breakdown of the issues, and compare to my final EICR, just to show how pointless many of these certificates are...

This was for a 17 year old new build too, so shouldn't really have been complicated....

Highlights so far are:

C3 for no access to meter or main fuse (which were in an external cupboard beside the main door)
ticked as TN-S when it's clearly marked PME in the meter cupboard (had they found it!) and has a low Ze
noted as 10mm earth conductor when it's 16
Bonding to water ticked as fine when it was disconnected under the sink (and the water was plastic incoming anyway)
"Pass" for RCD protection in locations with bath and shower when no protection on lighting circuits (and supplementary bonding not in place)
C2 for a batten fitting pendant which had the cover round the wrong way (no idea why) - was quicker for me to fix it than type that out!

But there are literally dozens more issues with the report.

They did notice water damage to main switch, to be fair to them - so I went armed to change main switch and add RCBO to lighting. Only to discover that the downstairs lighting had Neutral to earth of < 1 Ohm (obviously not found by their 'testing'). Going back tomorrow to investigate fully but it appears that some numpty managed to cross wire earth/neutral between outside socket and outside lighting when they installed Ring spotlights.



IMG_20220627_181316.jpg


Left hand box is fed from downstairs lights
Socket to right is fed from downstairs sockets.

Not sure exactly how yet, but there is some neutral to earth shenanigans afoot and some sort of interlink, at least on earth, and likely on Neutral, perhaps via backfeed

Naturally they didn't spot this:

IMG_20220627_175256.jpg


This is the batten fitting that obviously didn't come with clear enough instructions 🤦‍♂️ Would have been quicker for them to fix it than note it down....

IMG_20220627_120442.jpg


The main switch was picked up though, so clearly they had the cover off:

Needed changing too!


Main Switch.jpeg



Of course they missed this in the airing cupboard:


IMG_20220627_132225.jpg



And apparently struggled to find the meter box (This is the front door)

IMG_20220627_123926.jpg


I sometimes wonder why I bother! I seriously think that if a check was made of every EICR for landlords in the last two years, 40% plus of them would have at least one error on that could be ripped to shreds in a court without ever viewing the property in question or doing any further investigation.

It's clear that some effort was put in, that's the most annoying thing. I'm wondering if the tester ran out of time, and the missing gaps were filled in by picking pieces of paper from a hat back at the office!

On a completely unrelated note, anyone know how good Efficient Home Energy Ltd are? Apparently they carry out landlord inspections and landlords prefer them because they also do Gas certificates.
 
Finishing off a few things today, and find this below the hob...

That loop is the gas line for the hob above.

Any gas safe engineers in who can say if that's OK under their rules? Apparently this firm gave a gas certificate quite happily too...

C2 or C3 for cables separated from non-electrical services.....?

IMG_20220628_143054.jpg
 
I wouldn’t code that at all.
not the neatest job in the world but what is the actual risk?
No real risk I guess - and actually reading 528.3 it probably is OK - since it says

"The wiring system shall be suitably protected against the hazards likely to arise from the presence of the other services in normal use"

Which I guess means not needing to consider the chances of a leak and a spark occurring when coding.

Seemed wrong to me on first sight, but always learning when doing EICRs..
 
To be fair it looks like the meter cupboard is very difficult to access bearing in the mind the hinge side and the metal fence around it.

Agree on the rest of it though!
Easy enough to open from the front door and read the Fuse type/size and earthing type though. And possible if fiddly for the seal fairy to pull the main fuse so I could change the CU main switch...

Actually a PAYG meter in there, so presumably someone was using a key in there regularly. Chances of DNO moving it are a big fat zero though, so coding would be pointless.
 