Fitted a standalone fused 30mA RCD unit today protecting a spur from existing circuit wired directly from MCB in CU. RCD FCU is mounted adjacent to CU. CU has 100mA RCD upfront (Crabtree) & is populated by 60898 MCBs. 30mA RCD x1 test was fine (28ms) but the x5 test trips 100mA as well as 30mA RCD with a result of 41.80ms. Test is carried out from new socket outlet. Furthermore, if the 100mA RCD trips, upon resetting it the 30mA RCD trips of it's own accord.
Anyone have any ideas as to what might be occuring? Cheers
 
Is this a domestic property?
if it is why have you got a 100mA RCD - change this to a 30mA and forget the 2nd RCD - the 1st will protect it.

Easier and cheaper for you and the customer.
 
Is this a domestic property?
if it is why have you got a 100mA RCD - change this to a 30mA and forget the 2nd RCD - the 1st will protect it.

Easier and cheaper for you and the customer.

It is a domestic property, 100mA RCD already in situ, one of the older style RCDs (big chunky thing that takes up about a third of the board). Felt it would easier to fit standalone RCD protecting part of install I'm concerned with rather than trying to source an old 30mA Crabtree chunky which would ultimately effect entire install.
 
What dont you change the whole board?
You can get fully loaded ones for less than £70 now - MK as well if that's the quality you want (Yes I have seen the posts about MK boards)

I have found that fully loaded CUs are now cheaper than some RCDs.
 
What dont you change the whole board?
You can get fully loaded ones for less than £70 now - MK as well if that's the quality you want (Yes I have seen the posts about MK boards)

I have found that fully loaded CUs are now cheaper than some RCDs.

If it was my own property then I probably would but it's not. At the end of the day the customer wanted an additional socket in their hallway which I provided within the regs, all tested etc and at about a quarter of the cost to fit & test a new CU.
 
Remove the 100mA RCD and test it that way - then re-install the 100mA RCD.

You cant guess at that, the EIC requires exact readings, if you guess at it, its not worth the paper its written on, and your neck is on the line if the RCD is faulty
 
they do only trip on the load side, but you can have extra current flow in the neutral return and that will trip it.
The RCD is looking for a difference of (100mA for a 100mA RCD or 30mA for a 30mA RCD), the difference can be on the line or the
neutral, but if there is a difference then it will disconnect the supply.
 
could just be a slight few millisecs between the 2 poles of the 100mA making contact.
 
I'll try it out just to see out of curiosity, but I would've thought unless there was a fault on the load side of the RCD then it wouldn't trip. If it's not supplying anything (no load) the RCD still has 230v on one side and 0v on the other yet it doesn't trip, when there's an inbalance under load it will trip. I still can't see really how the supply could trip it.
I am a bit tired mind you and could be having a senior moment !!!!!!!!!
 
Im thinking as the jibjob said the supply was knocking the RCD out, but when the MCB is turned off, cutting the power (also the isolator is off) - there must be a earth leakage between the CU and the isolator on the line side.

If this was on the neutral side the RCD will still be tripping out.

The other problem might be an issue with the cpc on the cooker circuit - do a Zs on that as well and a R1 + R2.

What supply do you have? TNC-S??
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

jibjob

Arms
-
Joined
Location
Cheltenham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Another RCD problem
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
jibjob,
Last reply from
Spazz,
Replies
16
Views
2,910

Advert

Back
Top