My boss asked me to check a tripping problem on an outside rcd socket. Apparently it has tripped several times when a car valleter plugged his pressure washer into it!

Done the usual checks. It was tripping correctly. No bad connections and was dry as a bone inside. The only problem was that it's a little stiff to get a plug into it.

Told my boss about it and he said to change it for a non-rcd outside socket and we'll put a locked enclosure round it so that the house manager at the premises would retain the key and allow only competent persons use it. This being a car valleter!!

I said that I wasn't happy doing that as the socket was being used by ordinary people and that the house manager wouldn't care who used the outside socket.

So do I just do as I'm told or start spouting off reg no.s at him.
 
Try HSE (& I MEAN HM HSE) requirements for the use of pressure washers.
Then see if it is OK to remove the RCD...
 
Sounds like my boss is passing responsibility on to someone who knows nothing about nothing.

Would it matter what was plugged into it though?
 
Try testing the pressure washer, maybe!!

Does it trip with anything else connected?

It's occassionaly used to charge electric mobility scooters!
And not sure if it trips with that. I have asked that the pressure washer needs a PAT test though just incase.
Did a ramp test and tripped at 22.5mA.
Don't see any problems there.
 
It's occassionaly used to charge electric mobility scooters!
And not sure if it trips with that. I have asked that the pressure washer needs a PAT test though just incase.
Did a ramp test and tripped at 22.5mA.
Don't see any problems there.
if thats what its doing off load on ramp then its good for continued service..(as long as it meets times and the manual test button works)..
i would have thought it was clear....:
the pressure washer and/or any associated extension leads being used....
 
if thats what its doing off load on ramp then its good for continued service..(as long as it meets times and the manual test button works)..
i would have thought it was clear....:
the pressure washer and/or any associated extension leads being used....

Enough to turn you to drink, man..........again :nono:
 
yet again I knew I was right and the boss wrong and he's got 20 more years experience.

MMmmmmmmmm!
 