Hi all,
I've always understood that using the anti-trip setting will normally give an inaccurate reading. However I wasn't so aware of level of it's inaccuracy..
My own tester is a KT64.When I've done a comparison test on it the difference between the non-trip and normal reading many times, and the difference in the reading was only ever up to a maximum of 0.1 ohm.
Today I finally received my Megger from one of my employers, and so I had a play with it today and thought I would check for the difference in readings on this kit.
I measured a Ze of 0.16 ohms, and when I turned it to anti-trip it jumped up to 0.63 ohms. I was somewhat amused that this kit could really apply nearly half an ohm in inaccuracy?? I re-tested a couple of times (allowing a bit of time between tests) and it maintained these readings.
I'm not necessarily concened about this, but I thought I would post on here to see if anyone else has checked out their tester and if the readings are similar to this??

I've always understood that using the anti-trip setting will normally give an inaccurate reading. However I wasn't so aware of level of it's inaccuracy..
My own tester is a KT64.When I've done a comparison test on it the difference between the non-trip and normal reading many times, and the difference in the reading was only ever up to a maximum of 0.1 ohm.
Today I finally received my Megger from one of my employers, and so I had a play with it today and thought I would check for the difference in readings on this kit.
I measured a Ze of 0.16 ohms, and when I turned it to anti-trip it jumped up to 0.63 ohms. I was somewhat amused that this kit could really apply nearly half an ohm in inaccuracy?? I re-tested a couple of times (allowing a bit of time between tests) and it maintained these readings.
I'm not necessarily concened about this, but I thought I would post on here to see if anyone else has checked out their tester and if the readings are similar to this??