If you take the domestic 230V and the standard Ze for a TNS of 0.8 ohms and using ohms law;
I = V / R you get a current of 287.5A
Where does the standard main 100A or 150A breaker fit into this?

Please excuse my naivety, I can't get my head around this and I probably need it spelt out to me :-) be gentle, again I am a rookie!!
 
Ah I follow you now. Thanks for answering the question, sometimes it just clicks lol.
 
If you take the domestic 230V and the standard Ze for a TNS of 0.8 ohms
Not a standard, a maximum - normally <0.2.

and using ohms law;
I = V / R you get a current of 287.5A
That will be the earth fault current, but as above - liable to be a lot higher.

Where does the standard main 100A or 150A breaker fit into this?
They're not breakers, just switches and rated CCC.
 
If you take the domestic 230V and the standard Ze for a TNS of 0.8 ohms and using ohms law;
I = V / R you get a current of 287.5A
Where does the standard main 100A or 150A breaker fit into this?

Please excuse my naivety, I can't get my head around this and I probably need it spelt out to me :-) be gentle, again I am a rookie!!
They don't. You'd be lucky to get a 100A supply for anything where the Ze is 0.4ohms or above.
 