Hi there hope you can shed some light.
Ive got a cooker rated at 3.5kw
A hob at 6.4 kw
Now if i look to apply diversity to this to run a single T and E to a cooker switch the from the switch to a click double cooker connection point.
is this correct?
3.5kw =15.2 A
6.4KW = 27.8 A
TOTAL = 43 A
With diversity applied I'm looking at 10a + 30% of 43a = 22.9 a
Cable run 18 m Clipped direct therefore 6mm to cooker isolator
Any advice is greatly appreciated.