Nonsense, it works just as well across multiple appliances as a single appliance. Each element in a single appliance is individually controlled exactly the same as if they were all in seperate appliances.

I had a fish and chip van at a festival last year, the total load of cooking appliances plus some downlights and fluorescents was 15KW, I worked happily on a 32A supply. My data logger recorded a max of ~30A whilst it was fully in use.

I have also clamp tested cheap electric hobs that allow near the stated full load current to be drawn. Not a very common occurrence I will admit, but I'll stick to what I said.
 
what would you say then Resu??
Baring in mind I am technically still a trainee...

Minimum cable size would actually be 2.5mm although you wouldn't find a circuit breaker to suit! Common sense says 6mm though, seeing as you are running a new circuit in anyway. This would future proof too (to a certain degree).
 
In a new kitchen scenario with plenty of sockets I never use a cooker isolator with a socket, I don't think 5 amps is a very realistic assumption although something like a 'fast boil' 3kW kettle would admittedly only be on for short periods, I just think it's better to keep the cooker circuit purely for the cooker.
 
Baring in mind I am technically still a trainee...

Minimum cable size would actually be 2.5mm although you wouldn't find a circuit breaker to suit! Common sense says 6mm though, seeing as you are running a new circuit in anyway. This would future proof too (to a certain degree).

2.5mm on a 25A MCB? then Ib<In<Iz, so circuit complies.
 