Hi folks
I am retired and only tend to read the weekly summaries. I read the long-winded thread re. the storage heater and MCB tripping (thread now closed) and wished to make a few different comments.
(a) measuring voltage on an arcing supply using a normal multimeter (even a true RMS Fluke) can be very misleading - the meter is trying to average (or compute the RMS value). Showing 210-230 volts may result from almost zero volts to 300 volts or even higher for the positive spikes if there are inductive loads around. So in this case you can't work out the power being dissipated in the 100 A main switch by simply multiplying an apparent "multi-meter read voltage drop" by the "average current".
(b) because the current is making and breaking (to some extent) you have a high frequency pulsing current of many amps through the MCB - which is not what they are designed to deal with. This will cause internal mechanical vibration and affect the tripping accuracy.
(c) someone excellently suggested a using a radio. A small (and cheap!) portable medium or long-wave AM radio is incredibly useful in hunting for arcing noise on supplies. When I was on a technical OFFER (the old Regulator) committee, I found that to be the best way to initially check for arcing on rural supplies.
(d) Finally, do not forget to take into account the incoming supply voltage. All appliances (including storage heaters) are now designed for 230 volts RMS that was agreed back in the 1990s. However, the UK ESI, unlike most of Europe, chose not to implement the 240 V to 230 V change - instead changing the +/- voltage tolerances to -6% and +10% (216 to 253 volts). I have found many places, especially close to rural renewable generation feed-in substations, where it regularly hovers around the 250 V mark (and sometime above 253 V!). This is especially the case near to straw burners, waste incinerators and windfarms who generate at night and who are allowed to increase their supply voltage (by +10% over nominal, I believe) in order to deliver their agreed power to the network - that needs to be better regulated. A large 3.5 kW storage heater will draw 15.2 A at 230 volts - a resistive load of c. 15 ohms - so increasing the supply to 250 V RMS will increase the current to c. 16.7 A (actually it would be a little less as the increased temperature of the heating element would increase the resistance slightly).
Just food for thought (and probably, responses and challenges!)
I am retired and only tend to read the weekly summaries. I read the long-winded thread re. the storage heater and MCB tripping (thread now closed) and wished to make a few different comments.
(a) measuring voltage on an arcing supply using a normal multimeter (even a true RMS Fluke) can be very misleading - the meter is trying to average (or compute the RMS value). Showing 210-230 volts may result from almost zero volts to 300 volts or even higher for the positive spikes if there are inductive loads around. So in this case you can't work out the power being dissipated in the 100 A main switch by simply multiplying an apparent "multi-meter read voltage drop" by the "average current".
(b) because the current is making and breaking (to some extent) you have a high frequency pulsing current of many amps through the MCB - which is not what they are designed to deal with. This will cause internal mechanical vibration and affect the tripping accuracy.
(c) someone excellently suggested a using a radio. A small (and cheap!) portable medium or long-wave AM radio is incredibly useful in hunting for arcing noise on supplies. When I was on a technical OFFER (the old Regulator) committee, I found that to be the best way to initially check for arcing on rural supplies.
(d) Finally, do not forget to take into account the incoming supply voltage. All appliances (including storage heaters) are now designed for 230 volts RMS that was agreed back in the 1990s. However, the UK ESI, unlike most of Europe, chose not to implement the 240 V to 230 V change - instead changing the +/- voltage tolerances to -6% and +10% (216 to 253 volts). I have found many places, especially close to rural renewable generation feed-in substations, where it regularly hovers around the 250 V mark (and sometime above 253 V!). This is especially the case near to straw burners, waste incinerators and windfarms who generate at night and who are allowed to increase their supply voltage (by +10% over nominal, I believe) in order to deliver their agreed power to the network - that needs to be better regulated. A large 3.5 kW storage heater will draw 15.2 A at 230 volts - a resistive load of c. 15 ohms - so increasing the supply to 250 V RMS will increase the current to c. 16.7 A (actually it would be a little less as the increased temperature of the heating element would increase the resistance slightly).
Just food for thought (and probably, responses and challenges!)