Hi. We had some building work done to the house a few years ago and we got an armored 10mm 3 core under the house, that comes from the consumer unit on one side of the house, all the way to the other side of the house. This cable is not connected to something and I am thinking about getting an electrician to use it to take power to a garage I have at the back of the garden. Can someone please tell me whether this cable can be used at all for this given that it is simply sitting on ground, under the house? (my house is a classic house build in the 1920s). Thank you.
 
If the cable is still in good condition then it should be fine for use with a typical garage or out house, though it would need another length joined on to bring it out far enough. You can get proper armour cable joining kits that even allow such a joint to be buried.

However, you should get someone in to do an 500V IR (insulation resistance) test on it first to see if it really is in good condition and also check the R1+R2 (cable conductor + armour looped together) is in keeping with the cable specification to show the armour has not rusted away either.

See if there are any sparkys on this site near you, they should be able to take a look and quote for the job as there could well be other factors depending on your power supply arrangement and the specifics of what you are planning to have in the garage.
 
Thank you for your answer, @pc1966 . We have not decided on this, but one other option we have is to ask an electrician whether this cable could be used for a 7kw electric car charger. My only concern is that the cable itself is simply lying on the ground under the house and was not clipped to the joists or other structures under the house and I do not know whether there are any regulations around this.
 
Thank you for your answer, @pc1966 . We have not decided on this, but one other option we have is to ask an electrician whether this cable could be used for a 7kw electric car charger. My only concern is that the cable itself is simply lying on the ground under the house and was not clipped to the joists or other structures under the house and I do not know whether there are any regulations around this.

So do you mean it is just lying on the ground in the floor void rather than buried?

From your initial question I thought you meant it was buried below the building.
 
So do you mean it is just lying on the ground in the floor void rather than buried?

From your initial question I thought you meant it was buried below the building.
Yes. Lying on the ground, under the floor. The two ends are accessible, but there is no access to, for example, clip it to something.
 
Yes. Lying on the ground, under the floor. The two ends are accessible, but there is no access to, for example, clip it to something.

There isn't an absolute requirement to clip cable, however it must be supported, which being on the ground would be, if it was accessible then it would need some restraint to prevent it being pulled away etc.

However the ends where it comes up from the surface into the house/room needs to be supported properly, it shouldn't self-support.

If both ends are accessible you may be able to provide proper support, and perhaps rather than extending you could use it to pull the longer cable through.

If its going to be for an EVCP - note that these must be fitted with communication and most often a special transformer which must be fitted at the meter - so cable for EVCP tends to be combination type (power plus signal) you existing cable may not be suitable.
 
If its going to be for an EVCP - note that these must be fitted with communication and most often a special transformer which must be fitted at the meter - so cable for EVCP tends to be combination type (power plus signal) you existing cable may not be suitable.
Completely true, but there are also wireless options, so it might not be a total show-stopper.
 

Reply to Armored cable under the house in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
464
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
775
Trying to find an armoured cable behind plasterboard and studding. It was used to supply power from the house but has been disconnected Can...
Replies
2
Views
398
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
492

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock