bathroomboy

Got a job coming up soon, Wylex cu rewirables, need to rcd protect either lighting circuit or put local in rcd fcu, what would be the best method to do this at the board? Thanks.
 
Got a job coming up soon, Wylex cu rewirables, need to rcd protect either lighting circuit or put local in rcd fcu, what would be the best method to do this at the board? Thanks.

Quote them new CU and bonding too, if not already there. May aswell get them up to standard, then your ok if they ask you do do more work again :).
 
Not really an option, if they are paying a few grand for a new bathroom they don't want to pay for a cu upgrade, they can't understand why a few lights should cost so much. Cheers
 
Hey mate.

Could you not take the the lighting circuit out of the wylex board and have a 6A 30mA RCBO in a stand alone enclosure just for this circuit which you could feed off the now empty lighting fuse in the wylex board.

If not then a RCD FCU is probably the only way out.
 
Thanks for the replies, I'll see how it goes when I get on site, was in a merchants this morning and on offer split board complete £85 maybe in future I will offer to upgrade, price of a local rcbo is not cheap and when you consider the cost of a new board plus all the testing could be a better long term option.
 
Not really an option, if they are paying a few grand for a new bathroom they don't want to pay for a cu upgrade, they can't understand why a few lights should cost so much. Cheers

This says it all.
Happy to pay a few grand for a pretty new bathroom, but not a few hundred to protect their family.
 
Hey mate.

Could you not take the the lighting circuit out of the wylex board and have a 6A 30mA RCBO in a stand alone enclosure just for this circuit which you could feed off the now empty lighting fuse in the wylex board.

If not then a RCD FCU is probably the only way out.

Decided on 6A RCBO in stand alone enclosure due to wiring of the light switch (live common) would be messy to get another cable to it for switching, therefore only option is the Rcbo at the board, upstairs lighting fed from plug in mcb, am I ok to feed the Rcbo from this as it will then have two breakers on the same circuit.
 
Hey.

I dont see a problem with it, you will have your overload protection and fault protection for the circuit, as long as it's all clearly labelled up it's fine.

If you had installed an RCD FCU then there would be two overcurrent devices in the circuit, at least with this they are both at the mains position so minimising confusion if the lights do go out.

Cheers.
 

Reply to Bathroom Downlights in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock