Got a job coming up soon, Wylex cu rewirables, need to rcd protect either lighting circuit or put local in rcd fcu, what would be the best method to do this at the board? Thanks.
Discuss Bathroom Downlights in the Australia area at ElectriciansForums.net
Got a job coming up soon, Wylex cu rewirables, need to rcd protect either lighting circuit or put local in rcd fcu, what would be the best method to do this at the board? Thanks.
Not really an option, if they are paying a few grand for a new bathroom they don't want to pay for a cu upgrade, they can't understand why a few lights should cost so much. Cheers
Hey mate.
Could you not take the the lighting circuit out of the wylex board and have a 6A 30mA RCBO in a stand alone enclosure just for this circuit which you could feed off the now empty lighting fuse in the wylex board.
If not then a RCD FCU is probably the only way out.