EastAnglian
If the fuse pops on the perm live and the fan stops working then our poor homeowner might quite reasonably assume the thing is dead and receive a potentially fatal shock from the switched live which isn't as dead as it appears!
While not disagreeing with the need to fuse the switched line if a home-owner chooses to dismantle a fan without isolating it via the 3 pole switch first then any consequences are on their head. Aside from this, a 3A fuse will not protect a person from a potentially fatal electric shock, as it requires somewhere between 75 and 200mA (yes, mA) to cause the heart muscles to fibrilate if current flows through them. Shock protection is provided by your RCD which of course is designed to pop out at less than 30mA fault current.
If you touch the mains about the lowest resistance you will offer on any path that involves the major organs is 500 ohms, usually a lot higher like 2,000 ohms .... you will need about 38 ohms max to pop a 3A fuse, assuming it ruptures at about 2 x rating.