I am thinking of installing a Dyson AM04 bladeless fan/heater in an otherwise cold bathroom. The supply point
would be external to the bathroom and the circuit is RCD protected. The fan comes with a remote control to turn on/off
so there would be no direct contact with the heater.

I do not know the IP rating as yet but have contacted Dyson Support for the info.

Is there anything in the regs to indicate this is not acceptable.
 
On the face of it seems like a simple connect up if the heater is suitably IP rated and the feed is external to the bathroom.

Just ensure you get a Part 'P' registered electrican to install and issue the paperwork as being in a special location (bathroom) it falls under the building regs as "reportable".
 
So long as the fan is installed outside of the bathroom zones then it only needs to be suitable for the environment, this is where the information you get from Dyson could let you down; if they come back with IPX4 then OK, if less than that e.g. IP22 then you need to consider if it is suitable for a damp environment.
If the install is outside the zones then it is not notifiable in London (in England).
Other than that a 230V item of ventilation equipment outside the zones and on an RCD protected circuit and suitable for the environment would be OK.
 
....If the install is outside the zones then it is not notifiable .....

A very debatable point!!

As I understand it Part 'P' defines a location containing the bath/shower as the "special location" but the approved document itself just offers 'support' in how the building regs can be met.

The building regs refer to the zones defined within BS7671 -- normally taken as 0/1/2. You could argue that BS7671 defines outside Zones 0/1/2 as another zone, "outside the zones", so actually the building regs also refer to the whole of the location as a special location. That assumption aside, not following the Part "P" approved document is somewhat like saying BS7671 is a non-statutory document and you only need to follow for example the EAWR!

Technically correct and fine until something goes amiss then the arguement falls back onto why didnt you follow the recommendations of BS7671 -- one is assumed guilty under EAWR until you can prove yourself innocent and having followed the recommendations of BS7671 goes a long way to doing just that! I would suggest the same is true of following Part 'P' recommendations and treating the whole location as reportable not just within the specific zones.

To *******ise a well worn legal term, let the installer beware ...... but I know I shall be reporting everything within the location and not only the zones, just incase!!
 
I would say that this is not a debatable point, there is no problem if you wish to notify work outside the zones, but it is very clear that the Building Regulations do not require this.
The Building regulations state the specific area within which work is notifiable and it is not referenced to BS7671, it is stated independently and just "happens" to match the maximum extent of zones 0,1 and 2 in BS7671.

Extract from the regulations:
(6A)
A person intending to carry out building work in relation to which Part P of Schedule 1 imposes a requirement is required to give a building notice or deposit full plans where the work consists of—

(a) the installation of a new circuit;
(b) the replacement of a consumer unit; or
(c) any addition or alteration to existing circuits in a special location.

“special location” means—
(a) within a room containing a bath or shower, the space surrounding a bath tap or shower head, where the space extends—

(i) vertically from the finished floor level to—

(aa) a height of 2.25 metres; or

(bb) the position of the shower head where it is attached to a wall or ceiling at a point higher
than 2.25 metres from that level; and

(ii)horizontally—

(aa) where there is a bath tub or shower tray, from the edge of the bath tub
or shower tray to a distance of 0.6 metres; or

(bb) where there is no bath tub or shower tray, from the centre point of the
shower head where it is attached to the wall or ceiling to a distance of 1.2 metres; or

(b) a room containing a swimming pool or sauna heater.”.
 
Thanks guys for taking the time to respond much appreciated. Lets see what IP rating Dyson comes up with.
 
Just noticed your location Badged. You may still yet be correct.

What Richard Burns is referring to is the new part P document which was issued in April of this year which defines within the zones as the special location. The previous version defined the bathroom as the special location in line with BS7671. I do not think that the April changes were applicable to Wales, only England, so you may be working with the previous version in which case you were correct.

Can anyone confim/deny what I have just said ?
 
OK for Wales (my answer was only applicable to England as it says) it may be debatable to some extent.
The approved document and the building regulations do not agree.
In compliance with the wording of the building regulations it is fairly clear it is the zones so legal cover is assured.

The approved document P states special locations are:
Locations containing a bath tub or shower basin
Swimming pools or paddling pools
Hot air saunas

The building regulations state in this selected extract that it is the BS7671 zones (at the end of this extract):

Descriptions of Work where no Building Notice or Deposit of Full Plans Required

1. Work consisting of—
(a) replacing any fixed electrical equipment which does not include the provision of—
(i) any new fixed cabling, or
(ii) a consumer unit;
(b) replacing a damaged cable for a single circuit only;
(c) re-fixing or replacing enclosures of existing installation components, where the circuit protective measures are unaffected;
(d) providing mechanical protection to an existing fixed installation, where the circuit protective measures and current carrying capacity of conductors are unaffected by the increased thermal insulation;
(e) installing or upgrading main or supplementary equipotential bonding;
......

2. Work which—
(a) is not in a kitchen, or a special location;
(b) does not involve work on a special installation; and
(c) consists of—
(i) adding light fittings and switches to an existing circuit, or
(ii) adding socket outlets and fused spurs to an existing ring or radial circuit.

4. For the purposes of this Schedule—
“kitchen” means a room or part of a room which contains a sink and food preparation facilities;

“self-contained” in relation to a fixed building service means consisting of a single appliance and any associated controls which is neither connected to, nor forms part of, any other fixed building service;

“special installation” means an electric floor or ceiling heating system, an outdoor lighting or electric power installation, an electricity generator, or an extra-low voltage lighting system which is not a pre-assembled lighting set bearing the CE marking referred to in regulation 9 of the Electrical Equipment (Safety) Regulations 1994(1);

“special location” means a location within the limits of the relevant zones specified for a bath, a shower, a swimming or paddling pool or a hot air sauna in the Wiring Regulations, seventeenth edition, published by the Institution of Electrical Engineers and the British Standards Institution as BS 7671: 2008(2).
 
Thanks for that Richard. I am not disputing that you are right though, just trying to explain where Badged01's confusion may have arisen from.

On a separate note, just seen the price of those Dyson heaters, wow !
 