OK for Wales (my answer was only applicable to England as it says) it may be debatable to some extent.
The approved document and the building regulations do not agree.
In compliance with the wording of the building regulations it is fairly clear it is the zones so legal cover is assured.
The approved document P states special locations are:
Locations containing a bath tub or shower basin
Swimming pools or paddling pools
Hot air saunas
The building regulations state in this selected extract that it is the BS7671 zones (at the end of this extract):
Descriptions of Work where no Building Notice or Deposit of Full Plans Required
1. Work consisting of—
(a) replacing any fixed electrical equipment which does not include the provision of—
(i) any new fixed cabling, or
(ii) a consumer unit;
(b) replacing a damaged cable for a single circuit only;
(c) re-fixing or replacing enclosures of existing installation components, where the circuit protective measures are unaffected;
(d) providing mechanical protection to an existing fixed installation, where the circuit protective measures and current carrying capacity of conductors are unaffected by the increased thermal insulation;
(e) installing or upgrading main or supplementary equipotential bonding;
......
2. Work which—
(a) is not in a kitchen, or a special location;
(b) does not involve work on a special installation; and
(c) consists of—
(i) adding light fittings and switches to an existing circuit, or
(ii) adding socket outlets and fused spurs to an existing ring or radial circuit.
4. For the purposes of this Schedule—
“kitchen” means a room or part of a room which contains a sink and food preparation facilities;
“self-contained” in relation to a fixed building service means consisting of a single appliance and any associated controls which is neither connected to, nor forms part of, any other fixed building service;
“special installation” means an electric floor or ceiling heating system, an outdoor lighting or electric power installation, an electricity generator, or an extra-low voltage lighting system which is not a pre-assembled lighting set bearing the CE marking referred to in regulation 9 of the Electrical Equipment (Safety) Regulations 1994(1);
“special location” means a location within the limits of the relevant zones specified for a bath, a shower, a swimming or paddling pool or a hot air sauna in the Wiring Regulations, seventeenth edition, published by the Institution of Electrical Engineers and the British Standards Institution as BS 7671: 2008(2).