Hi all
I got called on to a job .It is external lights everytime i turned them on the fuzes keeps blowing done all the checks on the lights. To no end it still happens any ideas

The fuzes is on an old timer (contacter which turns them on ):rolleyes:
 
Hey.

When you say the fuses are blowing, which fuses do you mean? Is the circuit overloading - how many ouside lights - what size fuse.

Is there water in any of the fittings? Have you tried manually pushing the contactor on to see if they come on? Does this blow the fuse?

Have you tested the polarity of the contactor? Old ones can short between poles.

Cheers:D
 
Got 2 (fuses) on the contactor which is 10 amp fuses
which one runs five lights outside

The other fuses which is the same (10 amp fuses runs 8 lights outside)
No water in any fittings

Have manually pushing the contactor one set comes on then the fuse blows on the second one
 
Got 2 (fuses) on the contactor which is 10 amp fuses
which one runs five lights outside

The other fuses which is the same (10 amp fuses runs 8 lights outside)
No water in any fittings

Have manually pushing the contactor one set comes on then the fuse blows on the second one


Well you now know which circuit is causing the problem, it is down to stripping down each fitting to check for any damage, shorts etc.
 
Hi
split the circuit up and test IR you have a short somewhere, unless you see damage on the cable its a fitting or your contactor? take the lamps out for a quick check? what type of fittings are they?
 

Reply to Blowing the Fuze in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, Had an issue at a recent survey where doing a quick check and found we had pme with a reading of 0.44 ohms. Called the network and they...
Replies
5
Views
323
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
625
Hi guys. I will start by apologizing for the elementary question. I'm sure you get them often. The chandelier is in a hallway controlled by a...
Replies
6
Views
651
Hi, I've just had some electrical work completed in the bathroom; I've recently refurbished the bathroom, replacing the old electric shower with...
Replies
39
Views
8K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
576

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock