Nice to see some pics in progress, I'm looking on my phone so quite small pics but in pic 2 doing ZE what is your earth lead connected to? It looks like you haven't disconnected the main earth it looks like your testing all the flats earths? Could be wrong though small pics on phone, you look like that guy who won triple jump at the Olympics ( but slightly bigger :love:)
 
Not a critiscm glenn but how comes you put a main switch and an RCD in?
was just in the board....the board was a split load job...look at the neutral bars....

- - - Updated - - -

Nice to see some pics in progress, I'm looking on my phone so quite small pics but in pic 2 doing ZE what is your earth lead connected to? It looks like you haven't disconnected the main earth it looks like your testing all the flats earths? Could be wrong though small pics on phone, you look like that guy who won triple jump at the Olympics ( but slightly bigger :love:)
yep...well spotted onions....the pic i have allocated the Ze....was in fact the PEFC test....
 
was just in the board....the board was a split load job...look at the neutral bars....

- - - Updated - - -

yep...well spotted onions....the pic i have allocated the Ze....was in fact the PEFC test....

an eagle eyed onion! We'll pretend it was a ZDB instead, shhhhhhh no one will ever know.
 
For some reason i always pictured you as a thin wiry guy... lol!! I bet most picture me similar to your build, and probably bald too. How mistaken they would all be!! lol!!

Nice job Glenn, though it would have been better to have kept the bared conductor of the terminated cables to a minimum on the Neutral bar!!
if your on about the 25mm neutrals....they come like that with pre-formed ends...i think the strands are resistance welded together...or brazed or something....and i agree with you on em...their too long.....
 
He just called you fat :)

I think he said something about your mum too!

For some reason i always pictured you as a thin wiry guy... lol!! I bet most picture me similar to your build, and probably bald too. How mistaken they would all be!! lol!!

Nice job Glenn, though it would have been better to have kept the bared conductor of the terminated cables to a minimum on the Neutral bar!!
 
here onions....just for you;

Picture 010.jpg
 
Last edited by a moderator:
an eagle eyed onion! We'll pretend it was a ZDB instead, shhhhhhh no one will ever know.
a Zdb was carried out....
but if the PFC complies at the switchfuse....then its going to comply at the board..isn`t it....thats why i took the value there....
 
But a ZE not a ZDB
right:
the pic shows me carrying out a Ze to the property....i do this before any board change to confirm there is actually a proper earthing to the property...
now, this being flats after i had confirmed there was a good earth to the building i then got a Zdb at the board before replacing it...
the PFC i put down was the one i got when confirming the Ze in the pic....its going to be higher than the one i get at the board isn`t it...so as far as i`m concerned its covered...
hope this clears up any confusion.
Glenn.
 
Nice to see some pics in progress, I'm looking on my phone so quite small pics but in pic 2 doing ZE what is your earth lead connected to? It looks like you haven't disconnected the main earth it looks like your testing all the flats earths? Could be wrong though small pics on phone, you look like that guy who won triple jump at the Olympics ( but slightly bigger :love:)

Looks like you have lost your marbles again lol
 
I think onions is trying to say your are carrying out a zdb in your photo in your photo it shows all earthing cables to your earthing block, to carry out a true ze there should only be your main earth connected but you know that right lol nice neat job by the way good to see there are still some guys in the trade that take pride in there work :-)
 
Funky monkey wins the prize for translating my poor explanation. Marbles went a long time ago I think it was during the last pulling the main fuse debate zzzźzzzzzzź
 
I think onions is trying to say your are carrying out a zdb in your photo in your photo it shows all earthing cables to your earthing block, to carry out a true ze there should only be your main earth connected but you know that right lol nice neat job by the way good to see there are still some guys in the trade that take pride in there work :-)
no..the pic shows me carrying out PFC...thats why all the G/Ys are in the block....the other pic i posted shows me doing a Ze at the intake position....
i then went on to get a Zdb at the board .....
 