From my understanding you need to run both a 10mm earth from CU to water stop clock and seperate 10mm to gas, exception being if cable is uncut can link both gas and water together. In a scenario where been asked to change consumer unit but getting to gas pipes of combi boiler is practically impossible what are options. My thinking is that if water pipes tested and proved to be bonded correctly why would it not be feasible to link out water pipes and gas pipes of combi boiler. This then brings all pipework upto to same earth potential no?
 
From my understanding you need to run both a 10mm earth from CU to water stop clock and seperate 10mm to gas, exception being if cable is uncut can link both gas and water together. In a scenario where been asked to change consumer unit but getting to gas pipes of combi boiler is practically impossible what are options. My thinking is that if water pipes tested and proved to be bonded correctly why would it not be feasible to link out water pipes and gas pipes of combi boiler. This then brings all pipework upto to same earth potential no?
10mm2 main bonding conductor to the gas intake to the dwelling consumers side not at the Gas boiler, within 600mm I believe
 
BS7671 does not stipulate a continuous conductor. Can you verify bonds to both services.
 
10mm2 main bonding conductor to the gas intake to the dwelling consumers side not at the Gas boiler, within 600mm I believe
It's an old council block don't think there is any gas supply into properties, certainly not a gas cooker. If it only has a combi boiler does this mean that there is a gas supply? Confuses me to be honest my own property has no gas supply for cooking but they have run both 10mm to water and gas side pipes of combi
 
Combi boilers are predominantly gas however other fuels such as oil and electric can be used.
 
From my understanding you need to run both a 10mm earth from CU to water stop clock and separate 10mm to gas, exception being if cable is uncut can link both gas and water together.
They suggest continuous / uncut wire but I think any form of permanent join is acceptable, such as a crimp or solder. The concern (as I understand it) are screw joints loosening with vibration or temperature cycling.

My thinking is that if water pipes tested and proved to be bonded correctly why would it not be feasible to link out water pipes and gas pipes of combi boiler. This then brings all pipework upto to same earth potential no?
Relying on conductive pipes is a dubious thing, as often if a repair or upgrade is made the plumber will replace a metal section with some push-fit plastic stuff as it is quicker/easier/cheaper (to them).

Is there any bonding present now? Can you run a cable to the nearest accessible part of the gas pipe?
 
BS7671 does not suggest the bonding conductor to be continuous or give methods of how it should be made continuous. Guidance Notes do indeed suggest a continuous conductor however it does not cite a Regulation to support this.
 
BS7671 does not suggest the bonding conductor to be continuous or give methods of how it should be made continuous. Guidance Notes do indeed suggest a continuous conductor however it does not cite a Regulation to support this.
Agreed, I was looking at the guidance notes recently which shows this.
 
It's an old council block don't think there is any gas supply into properties, certainly not a gas cooker. If it only has a combi boiler does this mean that there is a gas supply? Confuses me to be honest my own property has no gas supply for cooking but they have run both 10mm to water and gas side pipes of combi
Surely if you have a gas boiler, stands to reason you have a gas supply/meter. other wise how are you charger for the gas you use
 
From my understanding you need to run both a 10mm earth from CU to water stop clock and seperate 10mm to gas, exception being if cable is uncut can link both gas and water together.

Bonding needs to be connected to all extraneous conductive parts at their point of entry to the installation. This is not necessarily limited to water and gas pipes, and not all water or gas supplies are extraneous conductive parts.
Bonding is not always 10mm, depending on the characteristics of the incoming supply or requirements of the DNO it can be bigger or smaller.
Bonding does not have to be seperate conductors to each service, nor does it have to be unbroken.
 
From my understanding you need to run both a 10mm earth from CU to water stop clock and seperate 10mm to gas, exception being if cable is uncut can link both gas and water together. In a scenario where been asked to change consumer unit but getting to gas pipes of combi boiler is practically impossible what are options. My thinking is that if water pipes tested and proved to be bonded correctly why would it not be feasible to link out water pipes and gas pipes of combi boiler. This then brings all pipework upto to same earth potential no?
It may do or it may not. If there was an insulating section in the pipework or a poorly conducting joint between the point of entry and the combi then it may result in unbonded extraneous pipe between the point of entry and the combi.
The whole point of bonding an extraneous service at the point of entry is that the hazard is introduced from outside, once within a building it is unlikely to pick up an external earth potential again. By bonding at the point of entry it can reasonably be assumed that the hazard is dealt with. That's not the case if bonding takes place elsewhere.
 
Where do people prefer to bond structural steel?
There is no ‘as close to entry point’ other than towards the ground and has multiple points but are usually connected together.
 
Where do people prefer to bond structural steel?
There is no ‘as close to entry point’ other than towards the ground
Usually at the most convenient place! Where there are a number of steel structures in the ground I do usually do a visual verification that various sections are bolted together and do an R2 test to a few sections after the bond is connected. Granted though in general little thought is given to bonding extraneous steelwork
 
Usually at the most convenient place! Where there are a number of steel structures in the ground I do usually do a visual verification that various sections are bolted together and do an R2 test to a few sections after the bond is connected. Granted though in general little thought is given to bonding extraneous steelwork
Admittedly I bond to the shortest route from the MET , as long as it’s accessible for I&T, whether this is completely the correct method, I don’t know?
 

Reply to Bonding combi boiler gas pipes in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
is it okay to bond the gas and water at the boiler?? Gas meter is tricky to get to, was going to just take a 10mm to water pipe at boiler and just...
Replies
6
Views
2K
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
885
Hi guys I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the...
Replies
6
Views
1K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock