Discuss Bonding gas/water yellow and blue in the UK Electrical Forum area at ElectriciansForums.net
It is up to the designer to decide what level of safety is required for the installation and so then specify the required level of resistance that is acceptable to determine the identification of extraneous conductive parts.
Generally 10mA is used because it is a catch all situation, not too bad not perfect.
If you have lots of large animals then less than 2mA may be the best approach, if there is minimal chance of any accidental contact and everyone in the area is adult then 30mA may be suitable.
I was thinking that might be in an industrial or commercial setting, but then the chance of accidental contact would probably be greater.
Yes it is, I forgotten you'd posted that. The two articles appear to be by the same author.
However, the one I posted has one difference, the example.
It suggests 'Based on the risk presented by the particular installation conditions, the relevant values for IB & ZTL, should be chosen from DD IEC/TS 60479-1', which as I haven't a copy, I guess are the figures given in GN8 6.1?
It then go's on to calculate RCP 'based on the 30mA (RCD)' for IB.
If you have a read, and see what you think.
As I read it, it’s not stating that a 30mA RCD has to be present, just that they are using the value of 30mA.
Here’s a graph based on the info from DD IEC/TS 60479-1:
AC-1: imperceptible
AC-2: perceptible but no muscle reaction
AC-3: muscle contraction with reversible effects
AC-4: possible irreversible effects
AC-4.1: up to 5% probability of heart fibrillation
AC-4.2: 5-50% probability of fibrillation
AC-4.3: over 50% probability of fibrillation
I did see that web page when I googled it this morning, but thanks for taking the time to post it.
Think I'll stick with the value given in GN8 6.1, got it in black & white (and I'm not paying $310 for DD IEC/TS 60479-1 either!).
Think GN8 is erring on the side of caution, but if I am subjected to litigation, I got a simple book I can produce in Court :)
re spinlondon's post:
The other problem is that the minimum CSA for an Earth conductor buried in the ground and not protected against corrosion by a sheath is 25mm2, 16mm2 if protected.
sureley that's for an earthing conductor, as in connected to a rod., not for a bonding conductor?
Where a protective conductor is buried in the ground, the Regulation for buried earthing conductors also applies.
New posts
Reply to Bonding gas/water yellow and blue in the UK Electrical Forum area at ElectriciansForums.net
Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
In a job today me and my colleague where discussing whether or not we had to earth the incoming water. It comes in blue pipe as you can see from...
4K
Good afternoon one and all. I, like many non-electricians are having issues regarding the need to have domestic water pipes (plastic entry to the...
5K