Hi I am recently qualified and still have a lot of learning/reading to do but Blue plastic waterpipe incoming, seems to always be a grey area with electricians I work with, me personally wouldn’t bond it..... Although we have to prove that in the plumbers install their is no copper going to earth?? Can someone enlighten me on this please

Many thanks..... and go easy on me lol
 
basically, you need to determine if any metal water pipes are extraneous. i.e. are they connected physically to the mass of earth. to do this, you set your MFT to IR test. test between the suspect pipe and your MET. if the reading is > 22k Ohms, then it does not require bonding.
 
basically, you need to determine if any metal water pipes are extraneous. i.e. are they connected physically to the mass of earth. to do this, you set your MFT to IR test. test between the suspect pipe and your MET. if the reading is > 22k Ohms, then it does not require bonding.

So does that mean only if they are accessible? And what if the blue plastic goes straight to white plastic? Would we have to take the bond over to the copper?
 
It’s highly unlikely that a mains water pipe entering a property in blue plastic then to copper will introduce an earth potential to the property unless said copper pipework is perhaps buried at some point in the ground.
Also when I ever see plastic incomers joining to copper say in commercial buildings and flats,the copper eventually joins to plastic again so it’s never necessary to provide protective bonding.
 
Of course there is the other viewpoint. In some point in the future that pipework after the plastic might be come ''extraneous' through refurbishments etc, so if you don't bond it from new (and it might get 'earthed' from parallel paths), and 10 years down the line it does become extraneous and requires bonding, how do you get a cable from the front to the back of the property. Just bond, and forget.
 
Of course there is the other viewpoint. In some point in the future that pipework after the plastic might be come ''extraneous' through refurbishments etc, so if you don't bond it from new (and it might get 'earthed' from parallel paths), and 10 years down the line it does become extraneous and requires bonding, how do you get a cable from the front to the back of the property. Just bond, and forget.
interesting viewpoint but you cant bond to start with if its plastic and you cant really forecast what might happen in future
 
Of course there is the other viewpoint. In some point in the future that pipework after the plastic might be come ''extraneous' through refurbishments etc, so if you don't bond it from new (and it might get 'earthed' from parallel paths), and 10 years down the line it does become extraneous and requires bonding, how do you get a cable from the front to the back of the property. Just bond, and forget.
When the 18th is published it looks like they have put it in black and white that if the incomer is plastic then doesn't need bonding.
 
It’s strange that every new build I see has now ditched the bonding to the water pipe as it’s plastic everywhere anyway but the gas still connects to the wall mounted meter outside in yellow plastic pipe.
Enters the property in copper but can’t see how it’s extraneous in that way?
Perhaps when the 18th is published they might not provide bonding to the gas anymore?
 
Hi I am recently qualified and still have a lot of learning/reading to do but Blue plastic waterpipe incoming, seems to always be a grey area with electricians I work with, me personally wouldn’t bond it..... Although we have to prove that in the plumbers install their is no copper going to earth?? Can someone enlighten me on this please

Many thanks..... and go easy on me lol
 
Thought that might generate some replies, by the way I wasn't suggesting bonding a plastic pipe.

All most every domestic dwelling I work in with a plastic water service and copper internals, has the copper bonded. This isn't new builds. Now that may be 'cos we've always done it that way, or ignorance, or because it was tested and found not to be extraneous.

So not bonding the metal element of a water service is correct, if when tested, is found not to be extraneous. What then if additional appliances (requiring cpc) are connected, which could change the results of that test, or the pipework is altered with the same result.

How do you now get a suitable cable to that point to bond it. How many of you test an existing install, to see if the existing pipework is extraneous, removing the water bond if necessary?

Not saying I'm right, just interested in the views of my more learned colleagues.
 
The point that is often missed in this kind of discussion is that the regulations apply to far more installations than domestic, and there are more things than just gas and water pipes which can need bonding.

It does keep things simple, in this case for the discussion.
 
In respect to your classic plastic incomer, sometimes it’s easier to bond it (the copper pipe work) than it is to prove it isn’t extraneous.
 
In respect to your classic plastic incomer, sometimes it’s easier to bond it (the copper pipe work) than it is to prove it isn’t extraneous.

Easier yes, quicker - maybe, but correct??
 
I think you will find that it says "if the water / gas pipe enters the house is of plastic construction, and the rest of the pipework is copper, then this copper must be bonded, are we not getting our wires crossed with the > than 22Kohms refers to supplementary bonding, not main bonding, open for discussion?
 
New posts

Reply to Bonding gas/water yellow and blue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
497
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
In a job today me and my colleague where discussing whether or not we had to earth the incoming water. It comes in blue pipe as you can see from...
Replies
15
Views
4K
Good afternoon one and all. I, like many non-electricians are having issues regarding the need to have domestic water pipes (plastic entry to the...
Replies
4
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock